Double Bus system with disconnectors 1

Status
Not open for further replies.

sparkview

Electrical
Nov 12, 2015
59
Hi all,

In a double bus system below. The normal operation is to use only Bus-I (disconnector DS-1A, DS-2A, and DS-3A closed and DS-1B, DS-2B, and DS-3B open).
While operating with load, can the disconnector of Bus-II, e.g., DS-1B be closed to open the disconnector of Bus-I, e.g., DS-1A?

Double-Bus-Single-Breaker-Scheme_rz4awp.png
 
Replies continue below

Recommended for you

It totally depends on what voltage and what kind of switch. No way to tell from the diagram.
 
Dear Mr. sparkview (Electrical)(OP)9 Jun 22 21:05
"....In a double bus system below. The normal operation is to use only Bus-I (disconnector DS-1A, DS-2A, and DS-3A closed and DS-1B, DS-2B, and DS-3B open). #1. While operating with load, can the disconnector of Bus-II, e.g., DS-1B be closed to open the disconnector of Bus-I, e.g., DS-1A? "
#1. No. Per IEC (disconnector=isolator) are designed for switching Without.
load/current.
#2. Attention: 1. The CB-1,2 or 3 MUST be open before operating on DS-1A, 1B; DE-2A, 2B ...

2. Check whether DS-1D, 2D which are by-passing the ES is allowed? Extremely dangerous!?
#3. It is usually NOT allowed that " DS-1B be closed to open the disconnector of Bus-I, e.g., DS-1A? "[/i]. See above #1. Not even Bus I and Bus II are from only one source/transformer.
#4. DS-1x shall be inter-locked with the respective CB-1. Also, CB shall be inter-locked with the respective ES.
Che Kuan Yau (Singapore)
 
DS-1B closed (when DS-1A is closed) but DS-3B and CB-3 shall be closed to couple Bus-B with Bus-A. Once done, DS-1A is opened and that completes changeover of feeder-1 from Bus-I to Bus-II.
The same sequence is repeated for other feeders also (to changeover all feeders (including sources) when Bus-I shutdown is planned.
 