Whaleotter
Electrical
- Feb 26, 2025
- 1
The utility I work for has multiple 13.8 kV ungrounded-Y 45MVAR shunt reactor installations that use a VCB for switching. The center phase Y connections on the VCBs have "doubled-up" 4-hole NEMA connections. The current flow is ~1900 Amps when the VCB is closed in. Recent IR surveys on several VCBs show slightly elevated temps on the center phase termination with Reactors switched in. I am looking for information on "doubled-up" NEMA pad terminations, whether this configuration is acceptable, and any information on ampacity ratings. See attached photo