I have an application with wide motor RPM and torque requirements and could use some help / verification. Here is what the motor shaft will see for loading.
Continuous Duty torque curve:
302 RPM @ 50Nm (37 ft/lb) ~ 1.5KW (2 HP)
1800 RPM @ 65Nm (48 ft/lb) ~ 12KW (16 HP)
2200 RPM @ 75Nm (55 ft/lb) ~ 17KW (23 HP)
3100 RPM @ 100Nm (74 ft/lb) ~ 33KW (44 HP)
Note: highest duty cycle is in the 1800-3000 RPM range
Load acceleration (Worse Case Overload)
218 Nm (161 ft/lbs), 11 second duration, repeats @ 5-minute intervals worse case.
Since motor weight is a large concern, the smallest commercial motor I have come up with is a 25HP, 4-pole motor wired for 230V/60Hz but supplied by a VFD at 460V/10-120Hz. I would like to use a totally enclosed aluminum frame, external blower cooled motor.
Questions:
1) Am I off base when pressing the 25hp motor through this load range?
2) With a 460V VFD running a 230V motor operating at low RPMs, will rotor heating be more of an issue than it would if the VFD was running a 230V input? As near as I can tell, the RMS current would be the same… Narrower pulses @ 460V vs wider pulses @ 230V.
3) What is the best way to calculate motor overload torque capability and duty cycle? I know what my load is doing, but what can the motor handle?
4) I’m looking at ABB and Siemens motors and ABB ACS 800 series VFDs … are there other motor or VFD makes I should consider in this application?
Thank-you, Bill
Continuous Duty torque curve:
302 RPM @ 50Nm (37 ft/lb) ~ 1.5KW (2 HP)
1800 RPM @ 65Nm (48 ft/lb) ~ 12KW (16 HP)
2200 RPM @ 75Nm (55 ft/lb) ~ 17KW (23 HP)
3100 RPM @ 100Nm (74 ft/lb) ~ 33KW (44 HP)
Note: highest duty cycle is in the 1800-3000 RPM range
Load acceleration (Worse Case Overload)
218 Nm (161 ft/lbs), 11 second duration, repeats @ 5-minute intervals worse case.
Since motor weight is a large concern, the smallest commercial motor I have come up with is a 25HP, 4-pole motor wired for 230V/60Hz but supplied by a VFD at 460V/10-120Hz. I would like to use a totally enclosed aluminum frame, external blower cooled motor.
Questions:
1) Am I off base when pressing the 25hp motor through this load range?
2) With a 460V VFD running a 230V motor operating at low RPMs, will rotor heating be more of an issue than it would if the VFD was running a 230V input? As near as I can tell, the RMS current would be the same… Narrower pulses @ 460V vs wider pulses @ 230V.
3) What is the best way to calculate motor overload torque capability and duty cycle? I know what my load is doing, but what can the motor handle?
4) I’m looking at ABB and Siemens motors and ABB ACS 800 series VFDs … are there other motor or VFD makes I should consider in this application?
Thank-you, Bill