Hello fellow Structural Engineers,
Thank you for your help,
GIVEN:
200x90 15" concrete PT slab.
The 200 ft direction is split 40-120-40 by two stairway cores.
In the 90 ft direction, the stairway cores split the length 45-45.
FIND:
So, in the concrete rigid diaphragm, do you put collector steel to the elevator core walls if they are in the middle (as described) of the PT slab?
POSSIBLE SOLUTION:
It would seem unnecessary in a case where you have a very deep diaphragm, and the core walls were at the midline.
As, I think it might get there by the strut & tie method? See Appendix A, pg 353 of ACI 318-05.
Multiple concrete struts in a 15" slab can take a lot of load.... but it would be a very long struct, i.e. column.
So, I am thinking I may have to use drag struts, with the OMEGA factor of 2.5, which adds quite a bit of steel, but at least I can go to #8's given the thickness of the slab.
RECOMMENDATIONS:
Any thoughts?
Thank you!
Mike in Seattle
Thank you for your help,
GIVEN:
200x90 15" concrete PT slab.
The 200 ft direction is split 40-120-40 by two stairway cores.
In the 90 ft direction, the stairway cores split the length 45-45.
FIND:
So, in the concrete rigid diaphragm, do you put collector steel to the elevator core walls if they are in the middle (as described) of the PT slab?
POSSIBLE SOLUTION:
It would seem unnecessary in a case where you have a very deep diaphragm, and the core walls were at the midline.
As, I think it might get there by the strut & tie method? See Appendix A, pg 353 of ACI 318-05.
Multiple concrete struts in a 15" slab can take a lot of load.... but it would be a very long struct, i.e. column.
So, I am thinking I may have to use drag struts, with the OMEGA factor of 2.5, which adds quite a bit of steel, but at least I can go to #8's given the thickness of the slab.
RECOMMENDATIONS:
Any thoughts?
Thank you!
Mike in Seattle