Drain Seal Pot Design

Status
Not open for further replies.

ukd

Chemical
Jun 15, 2006
20
NO
Hi,

I am wondering how to design a open drain seal/fire pot (installed for hazardous drain system)and what is the criteria that determines the water seal level? Is there any standard that is applicable to such?

Regards,
UKD
 
Replies continue below

Recommended for you

A parallel situation is the water seal in a flare drum to prevent flash back.
Looking in my notes, reference "A" calls for 6-inch min submergence.
Reference "B" calls for 3-4 inch submergence.
If your concern is flashback prevention, 3-6 inches of water seal should be a good design.
 