Powertester

Electrical
Jan 12, 2013
1
I have a customer that I am performing a load survey for. The purpose of this survey is to see how much current a three phase 400A feeder is drawing for one week. My customer would like to add load to this particular feeder. I received the data and noticed the min, max, and average data are very different. There are a lot of motor loads in this circuit. I realize there is going to be inrush current for each motor. Is the average RMS current the actual value I should use in my report? The average current was Approx. 180A and Max Current was 356A.
 
Replies continue below

Recommended for you

None of the above, what you need is the 15 minute demand current.
 