draw a curve of efficiency 1

Status
Not open for further replies.

faycalleroi

Electrical
Joined
Nov 30, 2012
Messages
10
Location
DZ
hello
in the aim to view the efficiency of induction motor variation with load variation i would know the formula of n(efficiency) and the P(power in shaft or load) to draw this curve example: for 10% 15% 20% 25% 30% 35%........OF P power what is the efficiency
best regards
 
A motor has fixed losses and load dependent losses. Load dependent losses vary with the square of the current.
The current has a magnetizing component that may be taken as fixed for a simple graph and a real component that varies with the load.
There is a "sweet spot" of greatest efficiency normally at about 50% to 75% load but often closer to 75%.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
There is an interesting mathematical excercize to find the location of max efficiency if we ASSUME that the losses are divided into two categories:
A - losses that are constant with respect to load
B - losses that vary with load^2 (I^2*R losses vary approximately with load^2 at high load... at lower load the approximation is not as good but will not matter if we're evaluating behavior at high load).

This suggests the model:
L = A + BX^2
where
L = total losses
X is power as fraction of full load power
A is no-load losses, excluding small losses due to stator I^2*R at no-load
B is load-related losses at 100% power (total 100% power losses minus no-load losses)

How do we maximize efficiency = Pout/(Pout+L)
where Pout =X*P100 and where P100 is rated output power

This should be the same as minimizing the inverse.
ie. minimize 1/effic. = (L+Pout)/Pout = L/Pout + P/P = L/Pout+1

The 1 is a constant and doesnt affect the minimization.
=> minimize L/Pout
minimize: L/Pout = [A + B*X^2] / [X * P100%] = [A/X + B*X] / P100

Since P100 is a constant with respect to X, it doesn't affect the minimization.
=> minimize [A/X + B*X]
Set derivative =0
d/dx{[A/X + B*X]} = [-A*X^-2 + B] = 0
A*X^-2 = B
A = BX^2
Xpeak=sqrt(A/B)

IF no-load losses were half the total losses, then A=0.5, B=0.5, peak efficiency would occur at 100% load.

Typically no-load losses are a smaller fraction. Let's say A = 0.33, B=0.67, then X = sqrt(A/B) = sqrt(1/2) = 1/sqrt(2) = 70.7%. Max efficiency would occur at 71%.

A useful model to think about, but not exact.


=====================================
(2B)+(2B)' ?
 