Hi everyone,

Does anybody know the difference between driving a conventional (regular reinforcement) pre-cast pile and pre-stressed pile, the conventional pile cross section is 10" x 10" and the pre -stressed is 12" x 12" (if there is a difference). Do we need different type of equipment to drive a pre-cast pile vs driving the pre-stressed pile.

Also, If there is a difference , how much roughly the cost difference would be per foot?

Thanks
 
Replies continue below

Recommended for you

I suggest that you call your local pile installer and ask. The answer will vary according to the equipment available in your area.

BA
 
The size may affect the pile driver to be used, but whether the pile is reinforced with piles or strands won't. As BA says, use your phone.
 
The big difference between "standard" and "pre-stressed" piles is the driving forces they can resist. When you drive a pile the energy wave that travels down the pile causes tensile forces at the bottom of the pile. Pre-stressed piles can resist a higher tensile force and therefor higher driving stresses. This allows for larger pile hammers to be used resulting in deeper driving and/or higher capacities without damaging the pile. Capacity and driving forces can be apporximated by your, or at least a good, geotechnical engineer.

So in a way there is a difference in the equipement used to drive the piles. As for the cost difference, call a supplier.

Also, there will be a capacity difference since the piles are a different size.

Mike Lambert
 
The prestressing is generally used to provide a compressive stress for the length of the pile. When the hammer strikes, a compressive wave is transmitted down the length of the pile. This reflects off the bottom of the pile and becomes a tension wave. The tensile wave can cause the concrete to crack/break. That's the difference... driven piles in these environs are generally tensioned. Pretensioned piles generally use a high strength concrete and are very elastic... the shockwave is readily transmitted.

If there is inadequate tensioning, the pile breaks and there is a 'puff' of 'dust' at the fracture point,,, generally above grade where there is little restraint from the soil to resist the tension wave.