Several questions come to mind about compaction of rockfill and the misplaced (in my opinion) about specifying a compaction level. You have not indicated if it is uniform size or is 500-600mm minus. Regardless,
1. In rock fill, you will have no binder - it will not have sufficient finer particles necessary to fill up all the voids - so that in every place you will, in effect, have a different material depending on how the material is distributed. You will also have large degrees of segregation.
2. If you have a required 90% relative compaction - relative to what? What tests are you running to get the MDD?? What material will you use given that every location will have a different degree of interlock - hence voids, etc.
3. How are you going to measure the in situ density after compaction? Digging a large pit, line with a impermeable membrane and fill with water for the volume?
4. Moisture control - with rock that big, any water you add will piss right on through.
I think that it would be better to specify a compaction sequence - such as 5 passes longitudinally using a 10 or 15 tonne vibratory roller, then 5 passes transversely, say. May then want to go back to a few passes of longitudinal.