rmae
Mechanical
- Aug 23, 2010
- 39
Hi,
I'm doing a design for an existing nursing home. Being a full NFPA 13 system the combustible attic space will require sprinkler. The building is existing (only 4 years old) and should have had sprinkler in the beginning but someone missed the requirement and permit was somehow issued and the building built and occupied.
The majority of the construction is vaulted ceilings which would lead to a nasty configuration of exposed piping. My intent, to the liking of the owners, is to utilize dry pendant sprinklers fed from the attic dry system.
My concern is, in Canada the applicable National Building Code of Canada (Code) requires that each sprinkler zone storey annunciate separately per 'storey'. By the Code an attic is not considered a storey however the definition of a storey is:
Storey means that portion of a building that is situated between the top of any floor and the top of the floor next above it, and if there is no floor above it, that portion between the top of such floor and the ceiling above it.
(note that the 'storey' ends at the ceiling, not the roof in the attic)
In your best opinion, do you think that I need to supply the dry pendant sprinklers serving the occupied floor level from a separate dry pipe valve (and hence separate zone) or would you consider the attic and the occupied floor area to be the same storey and hence one zone?
Comments and insight is greatly appreciated....
I'm doing a design for an existing nursing home. Being a full NFPA 13 system the combustible attic space will require sprinkler. The building is existing (only 4 years old) and should have had sprinkler in the beginning but someone missed the requirement and permit was somehow issued and the building built and occupied.
The majority of the construction is vaulted ceilings which would lead to a nasty configuration of exposed piping. My intent, to the liking of the owners, is to utilize dry pendant sprinklers fed from the attic dry system.
My concern is, in Canada the applicable National Building Code of Canada (Code) requires that each sprinkler zone storey annunciate separately per 'storey'. By the Code an attic is not considered a storey however the definition of a storey is:
Storey means that portion of a building that is situated between the top of any floor and the top of the floor next above it, and if there is no floor above it, that portion between the top of such floor and the ceiling above it.
(note that the 'storey' ends at the ceiling, not the roof in the attic)
In your best opinion, do you think that I need to supply the dry pendant sprinklers serving the occupied floor level from a separate dry pipe valve (and hence separate zone) or would you consider the attic and the occupied floor area to be the same storey and hence one zone?
Comments and insight is greatly appreciated....