There are two idential 550kVA transformers in an industrial plant. Durning a infared scan one core was recorded at 300F. They are 4160 delta/460 delta 220C insulation, 150C rise, dry type transformers. One is at 95% tap, the other at 100% tap. Tests on the transformer (power factor, excitation current, megger, turns ratio) showed simlar, normal results. A visual inspection did not show any burning of the insulation. The core ground was lifted and showed both cores grounded.
My explaination of the high temperature is circulating currents through the core because of the ground, shorting of the core iron causing excessive eddy currents, or heavy loading of the transfomer.
Currently the plant is going to mointor the temperature and see what it does. My questions are
What is the expected temperature of a dry transformer core? How hot is excessive? What is the best course of action. What would cause the excessive rise in temperature? I would appreciate any input.
My explaination of the high temperature is circulating currents through the core because of the ground, shorting of the core iron causing excessive eddy currents, or heavy loading of the transfomer.