Hello,
I’m currently supporting a project involving the replacement of an existing generator excitation system. The upgrade involves the installation of a new excitation xfmr, static excitation equipment (controls and power section), associated power and control cabling, etc. The specific question I have is related to sizing of the cabling between the secondary of the excitation xfmr and the AC input bus of the new excitation equipment.
The 3 phase excitation xfmr has a continuous rating of 2446 kVA, 4160V (primary) /540V (secondary). The xfmr (and the associated excitation equipment) has an occasional short-time overload rating of 3334kVA (for 10 seconds maximum). There is NO secondary protection OCD between the xfmr and the excitation equipment. The primary side OCD is a vacuum circuit breaker rated 1200A with an SEL 50/51 protective relay.
I am very clear on cable derating factors as it relates to ambient temperature, raceway design, etc. What there appears to some disagreement on in my group is the starting point for the calculations. Is it the xfmr nominal rating of 2446kVA or the short-time overload rating of 3334kVA? I have suggested the determination of secondary cable sizing starts at the 2446kVA and then in accordance with NEC we multiply by calculated current by 1.25 (in this case 3273 amperes/phase). After that, we consider cable ampacities and all the ambient temperatures, raceway design deratings, etc to determine number and size of cables per phase.
I’ve done some research but haven’t found anything definitive. I’ve been in plant operation for the past 13 years of my career and haven’t had much of an opportunity to do engineering design calculations like this in that time. I have however seen the long term results of under-sizing conductors and want to make sure we do it right.
Thanks in advance for your guidance.
I’m currently supporting a project involving the replacement of an existing generator excitation system. The upgrade involves the installation of a new excitation xfmr, static excitation equipment (controls and power section), associated power and control cabling, etc. The specific question I have is related to sizing of the cabling between the secondary of the excitation xfmr and the AC input bus of the new excitation equipment.
The 3 phase excitation xfmr has a continuous rating of 2446 kVA, 4160V (primary) /540V (secondary). The xfmr (and the associated excitation equipment) has an occasional short-time overload rating of 3334kVA (for 10 seconds maximum). There is NO secondary protection OCD between the xfmr and the excitation equipment. The primary side OCD is a vacuum circuit breaker rated 1200A with an SEL 50/51 protective relay.
I am very clear on cable derating factors as it relates to ambient temperature, raceway design, etc. What there appears to some disagreement on in my group is the starting point for the calculations. Is it the xfmr nominal rating of 2446kVA or the short-time overload rating of 3334kVA? I have suggested the determination of secondary cable sizing starts at the 2446kVA and then in accordance with NEC we multiply by calculated current by 1.25 (in this case 3273 amperes/phase). After that, we consider cable ampacities and all the ambient temperatures, raceway design deratings, etc to determine number and size of cables per phase.
I’ve done some research but haven’t found anything definitive. I’ve been in plant operation for the past 13 years of my career and haven’t had much of an opportunity to do engineering design calculations like this in that time. I have however seen the long term results of under-sizing conductors and want to make sure we do it right.
Thanks in advance for your guidance.