I've recently had a 12MVA dry type ventilated transformer fail. The transformer was a 34.5kV to 4160V which fed a 4160V starter lineup which feeds several pump motors. Transformer is 150C rise design, insulation class 220, manufactured in 1996. The transformer was part of a unit substation with a fused primary disconnect switch, and a secondary main circuit breaker. There are no drives, soft starters, or other sources of harmonic currents on the bus. The bus was extensively monitored, and the max voltage harmonics on the primary were 1.3% THD and current harmonics were less than 1% THD. The transformer load was 7.7 to 10.8 MVA running with a maximum 15 minute average of a little under 9MVA. The primary volatge seldom exceeds 103% of the 34.5kV nominal. Room ambient max 30C.
There was no diferential protection, only primary and secondary overcurrents and the fuse in the disconnect. The primary timed overcurrent covers 6 substations, so has a relatively high setting.
The transformer suffered interturn secondary winding fault, after failure there were no grounds present on the primary or secondary but when the center winding was dismantled the low voltage windings closest to the core were cooked. The actual wire insulation was baked and falling (flaking) off, and the fiberglass inner tube was reduced to only the fiberglass, particularly at the top of the winding. (No epoxy)
We have a 10MVA and 7.5MVA which were purchased at the same time as this transformer, so a thermographic study of these transformers was done and we found that they were running with the core above the center winding over 220C. (Upto 239C measured)
We beleived there is a design flaw in these transformers so we sent the 10MVA unit to the manufacturer for a heat run test. (not originally preformed) We witnessed the tests and found the following results:
111% excitation no-load, center core 1" from winding top reached a steady state temperature of 186C, and the center coil low voltage winding on the first wrap at 15" from the top of the coil reached 98C. (Amb. 24C) Low voltage excitation loss rises 37.9C (This was calculated by the manufacturer using the measurements of winding resistance after shutdown)
full load test, (secondary shorted, full load primary current) center core 1" from winding top reached a steady state temperature of 152C, and the center coil low voltage winding on the first wrap at 15" from the top of the coil reached 202.6C. This RTD peaked at 209C, the excitation tests were done first, with the load test done second, I figure it reached 209C as the core cooled from the excitation test, and the windings increased form the load test. (Amb. 21.8C) Low voltage load loss rises 105.2C. (This was calculated by the manufacturer using the measurements of winding resistance after shutdown)
Combining the average temperature rises from the resistance measurement method using the ANSI formula gives only a 128.2C rise which is within the 150C rise design.
Now for the question, is there a way of combing the RTD measurements from the excitation rise and load rise tests to prove the hot spot is exceeding the 220C rating of the transformer? It would seem to me that the peak reading of 209C corrected from the 23C ambient to 40C ambient is out of limits already, as well 202.6C at 21.8C ambient.
I tried combining the LV winding RTD values using the ANSI formula for combining the average temperature rises and calculated a rise of 219C. Is this calculation valid?
The manufacturer has requested that the transformer be sent to a third party test lab for full voltage, full load testing at our expense.
Thank You
There was no diferential protection, only primary and secondary overcurrents and the fuse in the disconnect. The primary timed overcurrent covers 6 substations, so has a relatively high setting.
The transformer suffered interturn secondary winding fault, after failure there were no grounds present on the primary or secondary but when the center winding was dismantled the low voltage windings closest to the core were cooked. The actual wire insulation was baked and falling (flaking) off, and the fiberglass inner tube was reduced to only the fiberglass, particularly at the top of the winding. (No epoxy)
We have a 10MVA and 7.5MVA which were purchased at the same time as this transformer, so a thermographic study of these transformers was done and we found that they were running with the core above the center winding over 220C. (Upto 239C measured)
We beleived there is a design flaw in these transformers so we sent the 10MVA unit to the manufacturer for a heat run test. (not originally preformed) We witnessed the tests and found the following results:
111% excitation no-load, center core 1" from winding top reached a steady state temperature of 186C, and the center coil low voltage winding on the first wrap at 15" from the top of the coil reached 98C. (Amb. 24C) Low voltage excitation loss rises 37.9C (This was calculated by the manufacturer using the measurements of winding resistance after shutdown)
full load test, (secondary shorted, full load primary current) center core 1" from winding top reached a steady state temperature of 152C, and the center coil low voltage winding on the first wrap at 15" from the top of the coil reached 202.6C. This RTD peaked at 209C, the excitation tests were done first, with the load test done second, I figure it reached 209C as the core cooled from the excitation test, and the windings increased form the load test. (Amb. 21.8C) Low voltage load loss rises 105.2C. (This was calculated by the manufacturer using the measurements of winding resistance after shutdown)
Combining the average temperature rises from the resistance measurement method using the ANSI formula gives only a 128.2C rise which is within the 150C rise design.
Now for the question, is there a way of combing the RTD measurements from the excitation rise and load rise tests to prove the hot spot is exceeding the 220C rating of the transformer? It would seem to me that the peak reading of 209C corrected from the 23C ambient to 40C ambient is out of limits already, as well 202.6C at 21.8C ambient.
I tried combining the LV winding RTD values using the ANSI formula for combining the average temperature rises and calculated a rise of 219C. Is this calculation valid?
The manufacturer has requested that the transformer be sent to a third party test lab for full voltage, full load testing at our expense.
Thank You