Is there any special considerations to take into account for using a small transformer to step-up 208 3 phase to 230 3 phase in a very humid environment...as in 95% or so relative humidity? It would either be an 18 kVA for powering a group of pumps or 75 kVA for powering all of the pumps (21 total). Imagine a large aquatium and fish shop in Atlanta (hot).
 
Replies continue below

Recommended for you

Encapsulated cores transformers are available up through about 27 kVA. These would be fine to use in a humid environment. For your application, you need a autotransformer connection to boost the 208V to 230V. This would actually be quite a small transfomer if you use an autotransformer connection, since the voltage difference is small.

Check with GE, Cutler-Hammer and Square D. They can probably help you out.
 

On dpc’s suggestion, if a boost to 229V from 208V is adequate, two 120:24V 5kVA transformers in an open-delta arrangement could do it for a 75kVA load.

An issue may be enclosure susceptibility to corrosion; requiring units not “off-the-shelf.”
 