If only one of the dual cores are used on the secondary side of the measuring CT(MV-switchgear).

Is it better to short and ground the unused core or to just leave it open ?

Comments to drawbacks and benefits ?
 
Replies continue below

Recommended for you

There is no option. You must short the unused core and it's best to ground it as well. It will not influence the accuracy of the other core.

Leaving a CT open-circuited is NEVER an option, due to the chance for high-voltage and ultimately damage to the CT, personnel, other equipment, or all of the above.

 