Hello,
I was wondering if when sizing cables going through duct bank conduits, you were using this logic...
For example, 2x 3C-500MCM goes through their own respective conduit within the same duct bank.
I use Canadian Electrical Code, so i would use Table 2 for the allowable ampacity of not more than 3 conductors. Since the spacing between the conduits are spaced by at least 1 conduit overall diameter (and obviously by a cable overall diameter as well), i don't need any derating applied to that table due to having more than 3 conductors...
Chapter 12 on wiring methods covers all installation methods for cables except duct bank... i am 99% sure of what i bring here, i am just trying to confirm...
What confuses me is Appendix D which requires a lower ampacity, where you have proper schematic for multiple conductors per phase, but i believe this is applicable only when more than 1 cable per phase is required? Not for 2x runs feeding 2 different loads...
Thank you!
I was wondering if when sizing cables going through duct bank conduits, you were using this logic...
For example, 2x 3C-500MCM goes through their own respective conduit within the same duct bank.
I use Canadian Electrical Code, so i would use Table 2 for the allowable ampacity of not more than 3 conductors. Since the spacing between the conduits are spaced by at least 1 conduit overall diameter (and obviously by a cable overall diameter as well), i don't need any derating applied to that table due to having more than 3 conductors...
Chapter 12 on wiring methods covers all installation methods for cables except duct bank... i am 99% sure of what i bring here, i am just trying to confirm...
What confuses me is Appendix D which requires a lower ampacity, where you have proper schematic for multiple conductors per phase, but i believe this is applicable only when more than 1 cable per phase is required? Not for 2x runs feeding 2 different loads...
Thank you!