Ductwork Best Practices

Status
Not open for further replies.

treits

Mechanical
Apr 29, 2016
2
I came across an installation today that I have not seen before. A round tap was installed directly on a radius elbow, since I have not seen this before I am curious if this is considered acceptable practice or if there may be airflow or noise issues as a result. Any opinions would be appreciated.
 
Replies continue below

Recommended for you

It is called a heel tap, It is not considered good practice, but every once in a while it has to be done. Normally if you, have, to do it. You try to offset the tap in the direction of the flow .
Good practice dictates that unless there is no other way, all fittings shall come off the straight duct.
I once got painted into a corner on a duct design , and ended up having to use a heel tap, My boss saw it and went ballistic , took the job away from me , then spent two days trying to re-draw the project without success, He finally gave it back to me and said , " Ok you can use it, but just this once.", so as you see it is not a popular solution.
B.E.

You are judged not by what you know, but by what you can do.
 
that is typical issue of contractor that has no even tiny sheet metal workshop able to make some custom-made fittings.
 