Dynamic fire damper listing

Status
Not open for further replies.

cme

Mechanical
Jan 16, 2003
196
I have been specifying Ruskin DIBD-2 fire dampers since I started my career

It has been brought to my attention that those dampers are not UL listed in horizontal installations for sizes larger than 24x24


Apparently this is the same for Prefco, Nailer, etc

What have you been specifying?
 
Replies continue below

Recommended for you

Use the multiple damper installation for larger openings. The openings can go up to 72x96.
 
Are multiple dampers UL listed?
 
The UL listing includes for installation of single or multiple dampers. The dampers would be interconnected such that a single fusible link activates them all.
 
the maximum size for a dynamically rated curtain type fire damper is 48x36 in the horizontal position ..... this is the maximum size UL will test for that application

else you have to go to a static rated curtain damper or a fire/smoke damper

one has to look at the free area and static pressure drop due to elbows, etc

i will post again when i get all the info
 