Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Dynamic System Monitor

Status
Not open for further replies.

aishu

Electrical
Jul 13, 2003
15
The question is whether Dynamic System Monitor (DSM) to be connected to metering core current Transformer (CT) or protection core. Metering core gets saturated during fault. However DSM manufacturers generally recommend Metering core CT. The problem with Protection Core is accuracy

Any Suggestion? What is the practice?
 
Replies continue below

Recommended for you

If you want to check the accuracy of the revenue metering you may want to use the metering CTs.
If you want information to analyze events you may want to use the protection CTs.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
If you are referring to a Digital Fault Recorder (DFR), I would connect to the protection CT's. I can't see much use for fault data full of saturated CT data (harmonics, flat top).

Enlighten us on what a Dynamic System Monitor is and what is the purpose of installing.
 