Hi everyone. I have a 7.5 MW power plant with 3 old generators units of 2.5 MW working in parallel directly attached to a 4160 V bus bar. One of the units is having Earth Fault trips as it is read in a CDG36 relay. The CDG36 coil current is the sum of the secondary three phase currents of the line CT’s in a wye configuration.
A Standby Earth Fault and Differential relays are present too, but none of them is giving trip signal. The Standby Earth Fault Relay is connected through a CT to the neutral wire of the generator and the Differential Relays have six independent CT’s.
Having checked the generator feeder and power connections, it was decided to mount a three phase Power Quality Analyzer on the very CT’s of the CDG36. All the measured variables in the three phases are each other consistent except for the power factor and the VAR in one of them. Mean while in the other two phases there is a lag power factor, the inconsistent one has a lead power factor with equal magnitude of current related to the other ones.
Provided there is a Standby Earth Fault protection, it was decided to lock out the e/f element of the CDG36 and keep running the unit until a suitable solution was found.
Any feedback from you would be very helpful. Thanks in advance.
A Standby Earth Fault and Differential relays are present too, but none of them is giving trip signal. The Standby Earth Fault Relay is connected through a CT to the neutral wire of the generator and the Differential Relays have six independent CT’s.
Having checked the generator feeder and power connections, it was decided to mount a three phase Power Quality Analyzer on the very CT’s of the CDG36. All the measured variables in the three phases are each other consistent except for the power factor and the VAR in one of them. Mean while in the other two phases there is a lag power factor, the inconsistent one has a lead power factor with equal magnitude of current related to the other ones.