jraef,
yes they are e-stops and labeled as such. I could find nothing in OSHA that prohibits the use of the guards. I did however contact NFPA yesterday and they sent me the following:
"Thank you for your email. Section 10.7.1.1 requires that all stop pushbuttons be readily accessible.
The term readily accessible is defined as "capable of being reached quickly for operation...". Accordingly, anything placed on top of or surrounding the button that inhibits its quick operation would not be permitted. And, since the button is required to be a mushroom head operating device in accordance with 10.7.4, it could be interpreted that concealing or sleeving the mushroom head would be prohibited also. Even though the NFPA 79 text does not specifically prohibit the use of an open front protective sleeves that do not cover the operating button head, the committee and I strongly urge users not to use them, since sleeves could effectively defeat the safety features afforded by a mushroom head operator and thereby inhibit quick operation of the emergency stop
I hope this satisfies your concerns. Please understand that this has not been processed as a Formal Interpretation, it must be considered as my personal opinion. Please see the statement below.
Very truly yours,
Joseph V. Sheehan, P.E.
Principal Electrical Engineer
Important Notice:
This correspondence is not a formal interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author, and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should it be relied upon, to provide professional consultation or services.
NFPA's mission is to reduce the worldwide burden of fire and other hazards on the quality of life by providing and advocating scientifically-based codes and standards, research, training, and education."