Arrangement is a Zn earthing transformer on 11kV busbars, feeder breaker with residual EF feeding at a distance a Delta/Wye transformer with HV fuses
If we assume that for a single phase EF the EF current is 3Io then as I see it the feeder EF relay will see 3Io and each of the phase fuses on the transformer will only see Io if the fault is between the fuse and the transformer.
Thus if you were tripping at, say, a 30A fault at the feeder then the fuse is only seeing 10A and, on a HV distribution transformer, may never trip and hence you have no discrimination.
Are these phase currents correct? Do you agree with my reasoning?