Ungrounded 11kV system is grounded through a neutral earthing transformer(NET) with impedance of 63 ohms/phase and neutral earthing resistor(NER)of 21 Ohms which yields an earth fault current of 151 Amps if NET impedance is added to NER i.e.
3xVp-n/(63+3x21) but if I consider resultant impedance of NET and NER then i get earth fault current of 213 Amps i.e. 3xVp-n/(sqr root of [63x63+63x63]).
Please advice if method is right.
Please note to make it simple i have ignored source impedances.
3xVp-n/(63+3x21) but if I consider resultant impedance of NET and NER then i get earth fault current of 213 Amps i.e. 3xVp-n/(sqr root of [63x63+63x63]).
Please advice if method is right.
Please note to make it simple i have ignored source impedances.