alingstone
Electrical
- Jun 30, 2009
- 14
Hi, I have a 22kV source transformer 66/22 Dyn3, and downstream of the 22 I have a 22/11 grounded auto-transformer Yna0. If I have a single phase to ground fault on the 11kV side of the auto-transformer of magnitude (say) 100A, how many earth fault amps will the 22kV relay back at the source see, is it the full 100A or is it only 50A.