For IDMT relays with 3 off residually connected phase CTs I use following settings :
Plug Setting – PS ( Long Time Pickup ) = 10% of transformer rated current
Curve = IEC Standard Inverse
Time Multiplier – TMS = 0.1 ( for trip time of 0.297 sec at 10 x PS ).
On both electro-mechanical and electronic relays the above settings have been sufficient to prevent tripping due to harmonic currents caused by CT partial saturation during transformer energization.
I have an application where a Sepam 1000+S20 relay protects a feeder to a 2.5MVA, Dyn11 transformer. Upstream relay settings necessitate a lower Time-Multiplier than the normal 0.10 on the transformer feeder. ( Time Multiplier of 0.297 sec at 10 x PS for French relays.)
The Sepam 1000+S20 relay has 2nd harmonic restraint to reduce the risk of tripping due to the dc offset in transformer inrush current.
Does any one have experience on how low the Time-Multiplier can be to avoiding tripping on energization, assuming a Plug Setting of 10% and an IEC Standard Inverse curve when using electronic relays such as the Schneider Sepam 1000+S20 ?
Plug Setting – PS ( Long Time Pickup ) = 10% of transformer rated current
Curve = IEC Standard Inverse
Time Multiplier – TMS = 0.1 ( for trip time of 0.297 sec at 10 x PS ).
On both electro-mechanical and electronic relays the above settings have been sufficient to prevent tripping due to harmonic currents caused by CT partial saturation during transformer energization.
I have an application where a Sepam 1000+S20 relay protects a feeder to a 2.5MVA, Dyn11 transformer. Upstream relay settings necessitate a lower Time-Multiplier than the normal 0.10 on the transformer feeder. ( Time Multiplier of 0.297 sec at 10 x PS for French relays.)
The Sepam 1000+S20 relay has 2nd harmonic restraint to reduce the risk of tripping due to the dc offset in transformer inrush current.
Does any one have experience on how low the Time-Multiplier can be to avoiding tripping on energization, assuming a Plug Setting of 10% and an IEC Standard Inverse curve when using electronic relays such as the Schneider Sepam 1000+S20 ?