Hello,
If you have a setup where there is a 11kv/415V transformer feeding into a main circuit breaker, then on to a switchboard, what is the advantage of having an earth leakage CT on the neutral at the main circuit breaker point. The CT operates the shunt trip of the main circuit breaker.
Is there a situation where this CT would be an advantage to have?
The load of the switchboard will be primarily motors. A power factor correction unit is installed to compensate.
There IS a chance of 'back-feeding' this switchboard as it is linked to a second transformer at the low-voltage end.
Is it better to use a 4-pole breaker as the main circuit breaker rather than use a CT on the neutral? Or will the two be doing a different thing?
thanks,
marko
If you have a setup where there is a 11kv/415V transformer feeding into a main circuit breaker, then on to a switchboard, what is the advantage of having an earth leakage CT on the neutral at the main circuit breaker point. The CT operates the shunt trip of the main circuit breaker.
Is there a situation where this CT would be an advantage to have?
The load of the switchboard will be primarily motors. A power factor correction unit is installed to compensate.
There IS a chance of 'back-feeding' this switchboard as it is linked to a second transformer at the low-voltage end.
Is it better to use a 4-pole breaker as the main circuit breaker rather than use a CT on the neutral? Or will the two be doing a different thing?
thanks,
marko