scragger
Electrical
- Jun 19, 2002
- 1
I have been given the enviable? task of tracing several earth leakage faults in several medium to large shops, basically the bulk of the fault current (measured in the switchroom on an ammeter which I cannot confirm as to the accuracy. It is over 30 years old) is on the lighting circuits, the bulk of which are fluorescents with starters and ballasts although these are not that old probably 8-12 years. This is confirmed by literally turning off two of the fuseboards and the fault drops by about 5 amps.
We have carried out a random sample earth leakage test using a PAT tester and gained readings of approx 0.1 to 0.2 milliamps over 3 ballasts,however this does not allow for the control gear cooling down after isolation before testing, we have also "meggered" the fuseboard with the lowest reading being 4 megohms which although low is acceptable and this one circuit has no more of an impact than any of the others.
As you are aware this type of equipment gets extremely warm and I feel this is causing a breakdown in the insulation inside the gear, I have been told that we as a firm need to prove this to the client probably to allow the responsibilty to be passed to the lighting maintenance contractors.
I have found the info on this subject to be a little sparse?
and wonder if anyone has experience in this field and may have some useful insights as to the possible cause, also it only appears to be on older equipment, and do harmonics play a part in increasing the readings obtained at the sitchroom meter.
Thanks
We have carried out a random sample earth leakage test using a PAT tester and gained readings of approx 0.1 to 0.2 milliamps over 3 ballasts,however this does not allow for the control gear cooling down after isolation before testing, we have also "meggered" the fuseboard with the lowest reading being 4 megohms which although low is acceptable and this one circuit has no more of an impact than any of the others.
As you are aware this type of equipment gets extremely warm and I feel this is causing a breakdown in the insulation inside the gear, I have been told that we as a firm need to prove this to the client probably to allow the responsibilty to be passed to the lighting maintenance contractors.
I have found the info on this subject to be a little sparse?
and wonder if anyone has experience in this field and may have some useful insights as to the possible cause, also it only appears to be on older equipment, and do harmonics play a part in increasing the readings obtained at the sitchroom meter.
Thanks