I am working on a football stadium with 4 lighting towers. Each tower has a 120kVA power panel at the bottow with incoming directly from the MDB.
So along with the feeder cables, i have 4 isolated earthing conductors running from the MDB earthing bar to the earthing bar of each of the 4 power panels.
Making the sums, this is like 1Km of 150mm2 cables. I want to save that money to afford other things in the project.
For this i want to run only the normal feeder cables from the MDB to the remote power panels and make an earth pit near each of these panels and connect the earth bar to it.
The question is am i violating any code? Do i need ground fault protection in the remote panels or i can count on the magnetic trip of the breakers in the MDB?
One solution proposed to me is to use an armoured cable in the already installed ducts and use the sheath as earthing conductor, which works also because cost of armoured cable is < cost of 4C cable + 1/2C conductor. I find that second solution more attractive since armoured means also higher insulation = higher permissible current.
Regards.
Define Expensive: 17,000 USD for one 4P HT 3200 PACB.
I am working on a football stadium with 4 lighting towers. Each tower has a 120kVA power panel at the bottow with incoming directly from the MDB.
So along with the feeder cables, i have 4 isolated earthing conductors running from the MDB earthing bar to the earthing bar of each of the 4 power panels.
Making the sums, this is like 1Km of 150mm2 cables. I want to save that money to afford other things in the project.
For this i want to run only the normal feeder cables from the MDB to the remote power panels and make an earth pit near each of these panels and connect the earth bar to it.
The question is am i violating any code? Do i need ground fault protection in the remote panels or i can count on the magnetic trip of the breakers in the MDB?
One solution proposed to me is to use an armoured cable in the already installed ducts and use the sheath as earthing conductor, which works also because cost of armoured cable is < cost of 4C cable + 1/2C conductor. I find that second solution more attractive since armoured means also higher insulation = higher permissible current.
Regards.