jc4477
Electrical
- May 14, 2012
- 2
Hi,
I am assisting in the design of an earth grid that spans quite some distance ~400m x ~800m.
An issue that I have encountered is the reliance on equipotential bonds to provide earthing on long conveyor runs up to 300-400m as opposed to physically placing a principal earth in the ground and creating a grid for the whole run of the conveyor.
I have gone through what I can of Australian Standards and found a document ENA-EG1 for substation earthing to be very useful.
Currently the plan is to bond all cable trays and structures back to the switch room main earth and have a rod or 2 placed into the ground at each support structure but not link each support structure rod together underground ie 20 supports for a long conveyor and each support to have its own earthing rod tied to it but not bonding each rod together (each rod having calculated resistance to earth of ~100ohm).
I have tried to work out an equivalent circuit and realistically I don’t think much if any current will pass through the local earthing rods at each structure.
I can see a lot of issue with this arrangement and fear the earthing system will behave in some sort of battery or neutral situation that may not trigger protective devices quick. (if I had my way I would be bonding all rods underground to create some sort of grid back to the switchroom main earth)
1. Even with multiple rods at each structure I anticipate each support structure to have total resistance to earth via the local rod arrangement at ~20ohm, with a potential 415V single phase to Earth Short, what will happen?
2. Will the equipotential bond via the cable trays and structure, will this provide the path to earth triggering the protection devices?
3. Will the support structure rods do anything? If the support structure arrangement does nothing how high can the step and touch potential get?
Sorry for the long one I am confused.
JC
I am assisting in the design of an earth grid that spans quite some distance ~400m x ~800m.
An issue that I have encountered is the reliance on equipotential bonds to provide earthing on long conveyor runs up to 300-400m as opposed to physically placing a principal earth in the ground and creating a grid for the whole run of the conveyor.
I have gone through what I can of Australian Standards and found a document ENA-EG1 for substation earthing to be very useful.
Currently the plan is to bond all cable trays and structures back to the switch room main earth and have a rod or 2 placed into the ground at each support structure but not link each support structure rod together underground ie 20 supports for a long conveyor and each support to have its own earthing rod tied to it but not bonding each rod together (each rod having calculated resistance to earth of ~100ohm).
I have tried to work out an equivalent circuit and realistically I don’t think much if any current will pass through the local earthing rods at each structure.
I can see a lot of issue with this arrangement and fear the earthing system will behave in some sort of battery or neutral situation that may not trigger protective devices quick. (if I had my way I would be bonding all rods underground to create some sort of grid back to the switchroom main earth)
1. Even with multiple rods at each structure I anticipate each support structure to have total resistance to earth via the local rod arrangement at ~20ohm, with a potential 415V single phase to Earth Short, what will happen?
2. Will the equipotential bond via the cable trays and structure, will this provide the path to earth triggering the protection devices?
3. Will the support structure rods do anything? If the support structure arrangement does nothing how high can the step and touch potential get?
Sorry for the long one I am confused.
JC