Power0020
Electrical
- Jun 11, 2014
- 303
I wonder about the practice at 66 kV levels with usually one substation (source) at 220/66 kV with the 66 kV side star neutral earthed, however, the (load) or distribution stations will have a delta or unearthed star 66/22 kV.
This is not the case with 220 kV or higher voltages where both ends substations have transformer sides with star and neutral point solidly earthed.
What is the purpose of keeping the network with only on side having an earth return? or both sides? I guess it doesn't have much to do with the overvoltages rather than the fault current detection/split.
Any clues?
This is not the case with 220 kV or higher voltages where both ends substations have transformer sides with star and neutral point solidly earthed.
What is the purpose of keeping the network with only on side having an earth return? or both sides? I guess it doesn't have much to do with the overvoltages rather than the fault current detection/split.
Any clues?