Hey everyone,
I'm looking for interesting and possibile solutions which came out with my practice.
#1. SOIL MODEL
During the preparation of the soil model (one or two layer soil model), I have to pass through a multilayer soil model. According to the local country rules I suppose to consider and increase the upper specific soil resistivity value at depth “hc” (usually 0,5-1,2m depending of the soil freezing depth and it’s duration) with coefficient “qc” (1,2 – 2,5 and over depending of the weather conditions when the measurement was done; 1,2=wet soil after rain) as shown on attached picture.
I’m interesting do you know about such considerations and how they’ve been solved in the different countries.
Also I’m looking for a simple and easy for use software tools for calculating from field measurements (Wenner method) to multilayer soil model, and additional one from input multilayer soil data (after the described over manipulations) to the one and two layer data (which can be used as input data for the regular earthing system design softwate).
#2. SOIL CHEMICAL ACTIVITY
Do you know about good methodology for considering an increase of the earthing conductor minimal cross-section depending of the project live and the soil chemical activity (pH measurements). I met one, but it’s only for steel conductors, and even of that I’m looking for a comparison?.
#3. OLD CU WIRE FOR EARTHING
In one of my last earthing design projects, according to the Investor requirements I used an old Cu conductor (removed from OHTL after 30 years of use). It supposes to be oxidized, and even after brush cleaning I’m considering about its conductor-ground resistance. Does any one have experience with such problem? Do you know about comparison results or research result of new and oxidized copper wires used as earthing conductor? Do you know some thing about the old Cu conductor-ground resistance?
#4. Cu COATINGS
Typically I’m using uncoated soft drawn copper wire for earthing system design, but I have seen also coated ones to be used. What is your usual practice? In what cases I suppose to use coated one and what kind of coating is suggestible?
#5. EARTHING CLAMPS vs. EXOTERMIC WELDINGS
Does any one have made or know about comparison between earthing system resistance built with clamps and the same one build with weldings (if they work in the same external conditions)? With which one is reached lower earthing system impedance (if there is difference as I expect)? Which solution is better if we have to consider the earthing system transient over voltages as result of direct lightning?
About the last one I think that with the welded one the overvoltage will be lower and the distribution of it will be on wider area then the builded with clams.
I’m sorry for the bad English, but I believe that the technical part of this post will be more interesting for you?.
I'm looking for interesting and possibile solutions which came out with my practice.
#1. SOIL MODEL
During the preparation of the soil model (one or two layer soil model), I have to pass through a multilayer soil model. According to the local country rules I suppose to consider and increase the upper specific soil resistivity value at depth “hc” (usually 0,5-1,2m depending of the soil freezing depth and it’s duration) with coefficient “qc” (1,2 – 2,5 and over depending of the weather conditions when the measurement was done; 1,2=wet soil after rain) as shown on attached picture.
I’m interesting do you know about such considerations and how they’ve been solved in the different countries.
Also I’m looking for a simple and easy for use software tools for calculating from field measurements (Wenner method) to multilayer soil model, and additional one from input multilayer soil data (after the described over manipulations) to the one and two layer data (which can be used as input data for the regular earthing system design softwate).
#2. SOIL CHEMICAL ACTIVITY
Do you know about good methodology for considering an increase of the earthing conductor minimal cross-section depending of the project live and the soil chemical activity (pH measurements). I met one, but it’s only for steel conductors, and even of that I’m looking for a comparison?.
#3. OLD CU WIRE FOR EARTHING
In one of my last earthing design projects, according to the Investor requirements I used an old Cu conductor (removed from OHTL after 30 years of use). It supposes to be oxidized, and even after brush cleaning I’m considering about its conductor-ground resistance. Does any one have experience with such problem? Do you know about comparison results or research result of new and oxidized copper wires used as earthing conductor? Do you know some thing about the old Cu conductor-ground resistance?
#4. Cu COATINGS
Typically I’m using uncoated soft drawn copper wire for earthing system design, but I have seen also coated ones to be used. What is your usual practice? In what cases I suppose to use coated one and what kind of coating is suggestible?
#5. EARTHING CLAMPS vs. EXOTERMIC WELDINGS
Does any one have made or know about comparison between earthing system resistance built with clamps and the same one build with weldings (if they work in the same external conditions)? With which one is reached lower earthing system impedance (if there is difference as I expect)? Which solution is better if we have to consider the earthing system transient over voltages as result of direct lightning?
About the last one I think that with the welded one the overvoltage will be lower and the distribution of it will be on wider area then the builded with clams.
I’m sorry for the bad English, but I believe that the technical part of this post will be more interesting for you?.