EARTHING(GROUNDING) TANSFORMERS 2

Status
Not open for further replies.

arjang

Electrical
May 24, 2001
4
1.WHAT DO THEY DO EXACTLY?
2.IN WHICH SITE CAN I READ ABOUT THEM(AND ALSO SEE THEIR PICTURES)?

 
Replies continue below

Recommended for you

hello;

i dont know any site about this subject, but the way is that;

there are two point on transformer first one for netural ant safety grounding.

for grounding; first you have to use a cu plaque (1m*1m size) and you have to bury it to a ground. but first you have to measure ground resistance it must be max 1000 ohm(as i remember) if not you can chance the ground type.

netural also have same kind of plague, netural and grounding plaques must be burry opposite site of the transformer.


x TR x
netural plaque ground
 
Suggestion: References:
1. Mason C. R., "The Art and Science of Protective Relaying," John Wiley & Sons, New York, 1956, page 268 "Grounding Transformers"
Reference 1 includes the y-delta and zig-zag grounding (= earthing in some Countries or Territories) transformer explanations and applications. It features schemes without direct connections of grounding transformers to the feeder (or downstream power distribution network) having load being protected by the grounding transformer against ground faults.
2. Beeman D., "Industrial Power Systems Handbook," McGraw-Hill Book Company, Inc., New York, 1955, page 348 "Grounding Transformers"
The grounding transformers may be connected directly to the feeder (or downstream power distribution network), and then they are treated as normal transformers from the grounding protection schemes standpoint. Again y-delta and zig-zag transformers are treated. Zig-zag transformer is usually smaller since it does not have the secondary windings; however, it is rated for very short time of fault duration and then fault must be tripped. y-delta transformer is usually used for the longer fault duration to allow time for its clearance.
 