In electrical maintenance field there is a practise to measure Earth resistance of earth pit on periodic interval.

Is there any method to check/confirm the continuity of the earth conductor between earth pit (grid) to the equipments

Generally population of the electrical equipments are too large in industry,in that case what will be the pratical method.
 
Replies continue below

Recommended for you

Dear 7anoter4,

Thanks for guidance but as you well aware the earthing grid acroos the plant (industry)passing thr several steel structure and if we adopt current injection method, practically it's not possible.
If any other way to test it, let us know.
Thanks
 
Check clamp-on resistance meter at AEMC website. They have some technical info on the principles and suitability of this method.
 