AusLee
Electrical
- Sep 22, 2004
- 259
Hi,
A contractor is building two adjacent houses, each house has a pool, the two pools are formed of one large reinforced concrete pit with a reinforced concrete wall in the middle.
Once the ground works are complete, a fence erected along the mdian wall will separate the two pools. Essentially it is like a double kitchen sink basin.
The electrician is refusing to connect the earthing of the electrical installation of the house to the metal of the pool saying that if he does so he will be joining the electrical installation of the two houses.
Each house has a single phase supply, they are not on the same phase: the network rule state that the houses are connected each to phase for network balancing. So:
House 1 has incoming active A and Neutral N. The earth is made locally by connecting N to Earthg at the meter panel of House 1.
House 2 has incoming active A and (a separate netural cable of course) Neutral N. The earth is made locally by connecting N to Earthg at the meter panel of House 2.
I would therefore say that at the incoming side, the 'joining' of the installation is even worse, because the same neutral is connected to both eathes (the supply authority likes to multipli earth the neutral at each connection).
Inside each house the active, neutral and earth are seaparate and never join (TN-C-S system in european terminology or Multiple Earthed Neutral in Aussie terminology).
What could be so wrong in connecting the earth wires of the two houses to the same combined two-in-one pool structure?
A contractor is building two adjacent houses, each house has a pool, the two pools are formed of one large reinforced concrete pit with a reinforced concrete wall in the middle.
Once the ground works are complete, a fence erected along the mdian wall will separate the two pools. Essentially it is like a double kitchen sink basin.
The electrician is refusing to connect the earthing of the electrical installation of the house to the metal of the pool saying that if he does so he will be joining the electrical installation of the two houses.
Each house has a single phase supply, they are not on the same phase: the network rule state that the houses are connected each to phase for network balancing. So:
House 1 has incoming active A and Neutral N. The earth is made locally by connecting N to Earthg at the meter panel of House 1.
House 2 has incoming active A and (a separate netural cable of course) Neutral N. The earth is made locally by connecting N to Earthg at the meter panel of House 2.
I would therefore say that at the incoming side, the 'joining' of the installation is even worse, because the same neutral is connected to both eathes (the supply authority likes to multipli earth the neutral at each connection).
Inside each house the active, neutral and earth are seaparate and never join (TN-C-S system in european terminology or Multiple Earthed Neutral in Aussie terminology).
What could be so wrong in connecting the earth wires of the two houses to the same combined two-in-one pool structure?