Distribution Standard of Eskom (Local South African electricity provider) re MV and LV reticulation earthing:
(reference SCSASAAL9)
4.2.2 Transformer installations
Distribution equipment associated with trsf installations that is either ground-mounted or pole-mounted and fed by underground cable or overhead line, shall be installed, connected and earthed in accordance with the following requirements:
a) Star point of trsf LV winding shall be earthed,
b) MV surge arresters, trsf tank and other metalwork shall be bonded to the MV earth electrode,
c) a combined MV/LV earth electrode may be employed only where the electrode resistance to earth does not exceed 1 ohm,
d) where seperate MV and LV earths are used:
1) MV and LV earth electrodes shall be seperated by not less than 5m,
2) a Neutral surge arrester shall be installed between the LV neutral terminal and the transformer tank and
3) care shall be exercised to ensure that there is no metalic or other low impedance conducting path between the MV and LV earths,
e) a Consumer's bare earth continunuity conductor in contact with the earth and of sufficient length might sometimes produce a low low enough earth resistance value to exclude the need for an LV earth electrode. However, this shall be confirmed by measurement.
The combination of MV and LV earths into a single electrode was the preferred earthing scheme at Eskom until the early 1980s. At this time, a new Code of Practice was published which exposed a hazard of shock that would be presented to customers in the event of power frequency current flow through the combined earth electrode. Today, a combined electrode shall only be installed where the electrode resistance to true earth is no more than 1ohm.
The 1ohm resistance criterion is specified in order to limit to a safe level the 50Hz voltage rise of the LV neutral in the event of a fault between MV phase and the transformer tank or core. For such a fault, the condition of raised potential on the LV neutral will remain until operation of MV earth fault protection.
It is important to notice that the 1ohm criterion is derived to limit the power frequency voltage rise of the LV neutral.
The hazard of high transfer potentials on the customer neutral in event of a power frequency current discharge through the MV/LV earth is largely averted by the use of seperate MV and LV earths. In avoiding one hazard, however, the seperation of the MV and LV earth electrodes introduces a hazard of its own.
The hazard from seperate electrodes is realized during high frequency discharges by the MV surge arresters. During these times, the potential of the transformer tank is raised to the voltage drop across the MV lead inductance and the MV earth electrode impedance. High tank potentials stress the insulation between the LV windings and the transformer tank and core. Over time continued insulation stress may lead to transformer failure.
Regards
Ralph