In any power system, the earth fault current goes to several kiloamperes and earthing resistance of 0.5 ohm is quiet common at a substation.
if that is the case, a circulating current between source and fault of say 10 kA and a resistance of 0.5 + 0.5 = 1 ohm leads to a power loss of about 100 MW! (I^2R)
Faults can last for up to 2 seconds and a reasonable power is dissipated, the question is :
where does this huge amount of power go? and if this is the case, the fault power is so high to cause generator rotor angle to stall (What happens is usually the opposite!)
I believe something is wrong with my understanding, any clue?