Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Earthing Transformer (zigzag) Hi-pot Testing questing

Status
Not open for further replies.

Latango

Electrical
Dec 12, 2006
28
0
0
AU
Just a quick question, had a search through and couldn't find an answer:

By IEC60076, when doing a separate source voltage withstand test on a transformer, all terminals of the winding under test must be connected together, and all other windings / metal parts, etc have to be connected to earth. Does that hold true for ZN transformers too? Since the N of the winding is designed to be earthed, does it need to be earthed for hi-pot?

Thanks for any help,
Mat
 
Replies continue below

Recommended for you

No, you are purely testing the insulation of the winding to earth. If you earth the neutral terminal during SS you would be testing zero sequence impedance (and drawing a lot of amps!). Just be sure to check the rating plate for the insulation level. Some terminals which are designed to be earthed have reduced clearance, eg. SWER, you can usually tell by the size of the bushings.
 
Status
Not open for further replies.
Back
Top