Hello all,
I have some questions regarding an eccentric column load on a strip footing.
Background: Residential home constructed 5 yrs ago, main floor beams designed to be installed in beam pockets in the concrete foundation wall. At one beam location, beam pocket was not cut out of the foundation wall. The framer built up a 3 ply 2x6 column under the end of the beam instead. The column is directly against the foundation wall, and sits on the footing. The basement slab was cast around the column. Fast forward 5 yrs, City requires a structural check of this column.
I have checked the beam and column itself, they can take the loads applied (main floor joist loads only, a 13.6kN (20kN factored) load on the column).
Drawings indicate the footing is 18"x6" with a 8" foundation wall. So, I am assuming the 5.5" base of the column is resting on 5" of strip footing on the inside of the wall, at an eccentricity to the footing centerline. e>(l/6), a large eccentricity.
I know a procedure for eccentrically loaded square or rectangular footing involving looking at the eccentricity as a point load plus a moment (P/a)+/-(M/S) to calculate the non uniform soil bearing pressure distribution.
However, I am not sure how to apply this to a STRIP footing. My questions to get me started are:
1) How does the load from the column distribute into the strip footing? i.e. what is the bearing area A in the (P/A)+/-(M/S) calculation? Will the load distribute at an angle through the 6" thick footing? Or will a length of footing "b" act as a rectangular footing of 18"xb?
2) Since the column seems to be "hanging" 0.5" off the edge of the footing, can I assume the column load as a point load at the centerline of column?
3) Since the eccentricity e>(l/6), I know the pressure calculated on the outside of the wall at edge of footing will be tensile i.e. the footing can lift. Are there any other checks I can do to confirm this? There is likely some steel in the footing, but drawings do not confirm spacing or grade.
Thanks for reading,
I have some questions regarding an eccentric column load on a strip footing.
Background: Residential home constructed 5 yrs ago, main floor beams designed to be installed in beam pockets in the concrete foundation wall. At one beam location, beam pocket was not cut out of the foundation wall. The framer built up a 3 ply 2x6 column under the end of the beam instead. The column is directly against the foundation wall, and sits on the footing. The basement slab was cast around the column. Fast forward 5 yrs, City requires a structural check of this column.
I have checked the beam and column itself, they can take the loads applied (main floor joist loads only, a 13.6kN (20kN factored) load on the column).
Drawings indicate the footing is 18"x6" with a 8" foundation wall. So, I am assuming the 5.5" base of the column is resting on 5" of strip footing on the inside of the wall, at an eccentricity to the footing centerline. e>(l/6), a large eccentricity.
I know a procedure for eccentrically loaded square or rectangular footing involving looking at the eccentricity as a point load plus a moment (P/a)+/-(M/S) to calculate the non uniform soil bearing pressure distribution.
However, I am not sure how to apply this to a STRIP footing. My questions to get me started are:
1) How does the load from the column distribute into the strip footing? i.e. what is the bearing area A in the (P/A)+/-(M/S) calculation? Will the load distribute at an angle through the 6" thick footing? Or will a length of footing "b" act as a rectangular footing of 18"xb?
2) Since the column seems to be "hanging" 0.5" off the edge of the footing, can I assume the column load as a point load at the centerline of column?
3) Since the eccentricity e>(l/6), I know the pressure calculated on the outside of the wall at edge of footing will be tensile i.e. the footing can lift. Are there any other checks I can do to confirm this? There is likely some steel in the footing, but drawings do not confirm spacing or grade.
Thanks for reading,