DMWWEngr
Structural
- Dec 2, 2001
- 74
I have a question about loads on slab-on-grades and the effect if has on items below grade.
Here's the situtuation:
I have a 40,000 lbs load that is essentially uniformly disrutbed over 8'x15' (120sqft).....imagine a water tank. This is to be placed on a 6" slab. 10+ft below grade there is concrete pipe that we do not want to place any (very little) additonal load on.
My boss, a non-structural engineer, is certain that this load cannot be applied and the slab will have to be competely redesigned. I have gone thorugh the calculations and I see no reason that this 6" slab (with S&T steel only) cannot support this load. I also went on to run an approximate check of the additional load to the pipe and I arrived at a 0.56% increase in load (not much at all).
Does this sound reasonable?? My boss is certian it will not work and I'm getting it will not be a problem at all. Am I missing something??
The additon of this load will also apply a lateral pressure to the wall. The wall is setup like this...The load will be applied to the top slab.
Load
/----------------
/
Grad / Earth
---------/
/
Earth /
/
There is a slight amount of "retaining wall" and the wall then extends down and is a footing. My questin is, where would you check for flexure of the wall?? Would you only look at the small retaining portion since below that the wall would be restained by the earth on the other side?? Would you treat it as pinned between the top of the wall (where these is a slab) and the earth??
I'm just looking for a little guidance. Thanks in advance.
Here's the situtuation:
I have a 40,000 lbs load that is essentially uniformly disrutbed over 8'x15' (120sqft).....imagine a water tank. This is to be placed on a 6" slab. 10+ft below grade there is concrete pipe that we do not want to place any (very little) additonal load on.
My boss, a non-structural engineer, is certain that this load cannot be applied and the slab will have to be competely redesigned. I have gone thorugh the calculations and I see no reason that this 6" slab (with S&T steel only) cannot support this load. I also went on to run an approximate check of the additional load to the pipe and I arrived at a 0.56% increase in load (not much at all).
Does this sound reasonable?? My boss is certian it will not work and I'm getting it will not be a problem at all. Am I missing something??
The additon of this load will also apply a lateral pressure to the wall. The wall is setup like this...The load will be applied to the top slab.
Load
/----------------
/
Grad / Earth
---------/
/
Earth /
/
There is a slight amount of "retaining wall" and the wall then extends down and is a footing. My questin is, where would you check for flexure of the wall?? Would you only look at the small retaining portion since below that the wall would be restained by the earth on the other side?? Would you treat it as pinned between the top of the wall (where these is a slab) and the earth??
I'm just looking for a little guidance. Thanks in advance.