i got an 18000 amp per leg ac electric arc furnace with bus cables over 3 years old with tens of thousands hours running time, our bus cable provider suggest we swap them out every 9 months or at 20% increase in resistance, which got me wondering, 20% increase of a cable newly rated at 0.033milliohms could cause some power problems, right?
say, 20% for each of the three legs at 18000 amps
p = (18000^2)*(.000033/.2) = 53460W
ptot = 53460 * 3 = 160.3kW
is that very bad figuring or very bad cables?