I am a consulting electrical engineer and have come across a design dilemma. We will take this to the AHJ, but I thought it would be nice to get some input from some code experts to see if I was on the right path.
We are working on an addition at a major airport and part of the scope are new generators and a fire sprinkler system with partial deluge sprinklers on some exterior curtain wall systems. This has resulted in the need for a 2000gpm system served by two new electrically driven, 125 HP fire pumps. No problem there.
What I am having a problem resolving is the number of overcurrent protective devices in the supply line to the Fire Pump controller/ATS.
ON THE GENERATOR SIDE:
The emergency power to the building is served from 2-1500kW diesel engine driven generators operating in parallel through a synchronizing switchboard. The 5000A, 480V, 3Ph, 4w, 60Hz switchboard has two draw-out type air circuit breakers that feed the two fire pumps via the ATS'. I have located these ahead of the main circuit breaker. The Life Safety, Smoke Control, Mechanical and I.T. branches are fed downstream of the main.
My first question is this. Since I have non-automatic breakers at the generators for maintenance purposes, and then the synchronization breaker at the switchgear, is it a problem to have the generator feeder breaker for the generators? NFPA 20, 9.6.1.2 states that "A tap ahead of the on-site generator disconnecting means shall not be required." So are the three disconnecting,(two being overcurrent devices), violate the limitation of the number of overcurrent devices in a Fire Pump feeder?
NORMAL POWER FEEDER:
This is more complicated. We have a 34.5kV on-site distribution system. The buildings are fed by a series of 34.5kV-480Y/277V,3Ph,4w substations which in turn feed into double ended MAIN-TIE-MAIN 480V distribution switch boards.
Normally I take the Fire Pump ATS feeders primary to the 480V main and follow standard Fire pump control protocol. My problem is in figuring out a control sequence since these switchboards are source transfer, redundant switchboards. If my Fire Pump feeders are ahead of Main #1 and everything is running normally, that is ok. But if for some reason Main #1 is opened or for any reason service #1 is off-line the system is designed to automatically transfer to service #2, and my Fire pumps are without power. Obviously that cannot happen. I can take a feed from each service, but then under normal conditions they are both hot. This cannot be a new condition, All I can see is that I need a second layer of transfer switches for the normal power feeder from the two services.
There must be some simpler way, has anyone done this? I feel I am missing something basic.
Thank you in advance for any input.
Regards,
EEJaime
I am a consulting electrical engineer and have come across a design dilemma. We will take this to the AHJ, but I thought it would be nice to get some input from some code experts to see if I was on the right path.
We are working on an addition at a major airport and part of the scope are new generators and a fire sprinkler system with partial deluge sprinklers on some exterior curtain wall systems. This has resulted in the need for a 2000gpm system served by two new electrically driven, 125 HP fire pumps. No problem there.
What I am having a problem resolving is the number of overcurrent protective devices in the supply line to the Fire Pump controller/ATS.
ON THE GENERATOR SIDE:
The emergency power to the building is served from 2-1500kW diesel engine driven generators operating in parallel through a synchronizing switchboard. The 5000A, 480V, 3Ph, 4w, 60Hz switchboard has two draw-out type air circuit breakers that feed the two fire pumps via the ATS'. I have located these ahead of the main circuit breaker. The Life Safety, Smoke Control, Mechanical and I.T. branches are fed downstream of the main.
My first question is this. Since I have non-automatic breakers at the generators for maintenance purposes, and then the synchronization breaker at the switchgear, is it a problem to have the generator feeder breaker for the generators? NFPA 20, 9.6.1.2 states that "A tap ahead of the on-site generator disconnecting means shall not be required." So are the three disconnecting,(two being overcurrent devices), violate the limitation of the number of overcurrent devices in a Fire Pump feeder?
NORMAL POWER FEEDER:
This is more complicated. We have a 34.5kV on-site distribution system. The buildings are fed by a series of 34.5kV-480Y/277V,3Ph,4w substations which in turn feed into double ended MAIN-TIE-MAIN 480V distribution switch boards.
Normally I take the Fire Pump ATS feeders primary to the 480V main and follow standard Fire pump control protocol. My problem is in figuring out a control sequence since these switchboards are source transfer, redundant switchboards. If my Fire Pump feeders are ahead of Main #1 and everything is running normally, that is ok. But if for some reason Main #1 is opened or for any reason service #1 is off-line the system is designed to automatically transfer to service #2, and my Fire pumps are without power. Obviously that cannot happen. I can take a feed from each service, but then under normal conditions they are both hot. This cannot be a new condition, All I can see is that I need a second layer of transfer switches for the normal power feeder from the two services.
There must be some simpler way, has anyone done this? I feel I am missing something basic.
Thank you in advance for any input.
Regards,
EEJaime