GB _
Industrial
- Apr 14, 2018
- 1
We had issues with motor brake failure after like replacement the original was a single voltage 460v motor with a rectifier that was wired for full bridge to the brake coil this was in service for ten years the brake coil went out we replace the motor and brake as one the new motor is a dual voltage 240/460v it was wired the same as the original motor the brake lasted two weeks we found our mistake in wiring the brake rectifier it should have been wired half wave my question is could the original motor brake been a 480v DC ? this seemed likely to us because of the single voltage motor rating and by wiring the replacement as original it is rated only 240 DC the replacement brake coil is marked AC 480v