Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Electric Motor Efficiency

Status
Not open for further replies.

sunilji

Electrical
Feb 17, 2001
28
Hi All,
I am searching for a modern, portable instrument for testing Efficiency of 3 phase Electric Motors in the range of 1 to 30 hp.
I welome replies from anyone with experience or information
Regards to All
 
Replies continue below

Recommended for you

As you may be aware there are quite a number of different ways to measure efficiency. See IEEE112.

I'm guessing that on the small horsepower range a direct measurement is best/easiest if you can find someway to measure the output power (shaft horsepower=brake horsepower).

Measuring the input power is trivial using any of a variety of instruments that measure current, voltage, and angle between them.

There are quite a variety of other more complex ways to do it without actually loading up the motor. Those are more attractive in the higher horsepower range where mechancial loading of the motor is difficult/expensive. These methods also offer a benefit of segregating the losses into the various categories... stator I^2R, rotor I^2R, core losses, frction and windage, stray losses.




 
there definitely is available in market meters with plug in type CTs which measure not only the instantaneous power but also kva,kvar,p.f.,V,I etc. I used one by ITT germany even one madras based firm markets one with printout option.















 