I received a call from a friend that his V'S is acting up and would like me to look at it. The VSD controls one 20 hp motor. The VSD is in fault mode showing over voltage. When I check the voltage it is correct with what is supposed to be present. "480/240 3 phase.
This system has 12 motors that are being fed from a plant generator.
I have isolated all 12 motors to check each one individually. When I energize on of the motors the phases go unbalanced, phase to ground readings L1/2.4 volts-L2/498 volts, L3/498 volt. I
I assume this high voltage feed back is what is causing the VSD to fault but is is the generator under load causing the problem or the one motor leaking due to bad windings or stater. Also the motor seems to be work fine with no visual problems.
This system has 12 motors that are being fed from a plant generator.
I have isolated all 12 motors to check each one individually. When I energize on of the motors the phases go unbalanced, phase to ground readings L1/2.4 volts-L2/498 volts, L3/498 volt. I
I assume this high voltage feed back is what is causing the VSD to fault but is is the generator under load causing the problem or the one motor leaking due to bad windings or stater. Also the motor seems to be work fine with no visual problems.