I am an electric utility engineer. On a 20 mile long 25kV distribution feeder, 336.4kcmil AAC Tulip phase conductor with a 7#8 Alumaweld neutral, peak load about 9MW around 200A/phase. We are having trouble with voltage unbalance. Eighteen miles out on the feeder we have a set of three single phase voltage regulators. Phase to ground voltage magnitudes are all being held well matched, but the phase to phase voltages are unbalanced and causing problems for some of our three phase customers. This problem has been here longer than I have, but we've never addressed it as the end of line customers are usually fed from a different source.
We have capacitor banks along the feeder. They all check out to be operating ok.
Our primary neutral conductors are grounded at every pole. The feeder runs down a chain of very narrow low elevation porous rock islands (Florida Keys), so lots of our pole grounds are in salt water.
What are all the probable causes for the phase to phase voltages to be unbalanced while the phase to ground voltages are all ok? I understand that the phase angles between voltages are not equal - is this all caused by unbalanced load, or should I be looking for other issues also?
K2ofKeyLargo
We have capacitor banks along the feeder. They all check out to be operating ok.
Our primary neutral conductors are grounded at every pole. The feeder runs down a chain of very narrow low elevation porous rock islands (Florida Keys), so lots of our pole grounds are in salt water.
What are all the probable causes for the phase to phase voltages to be unbalanced while the phase to ground voltages are all ok? I understand that the phase angles between voltages are not equal - is this all caused by unbalanced load, or should I be looking for other issues also?
K2ofKeyLargo