Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Electrical outlet standards

Status
Not open for further replies.

tspan

Mechanical
Jun 9, 2009
2
0
0
CA
Is there a standard on dimensions of a duplex receptacle on a single yoke? We are looking to manufacture an additional circuit to be added to the back of a standard 5-15 outlet which would give us wireless control over it. According to the NEC and NEMA the receptacle counts as 2 conductors multiplied by the volumetric allowance for the largest wire in the box. I need to know how much volume the receptacle can take up to maintain compliance. For example in a 18in3 electrical box with 2 14/3 wires how large an area may the receptacle (mounted on a single yoke) use. Is this regulated?

Thanks in advance,

Teresa
 
Replies continue below

Recommended for you

Thanks for that, I've actually read that standard and it regulates the face dimensions but not the depth. A NEMA representative suggested using GFCIs, etc as a guideline but as far as percentage of box thast can be filled or back clearance, it seems is not regulated.
 
Status
Not open for further replies.
Back
Top