Reesh14
Electrical
- Aug 3, 2005
- 38
I received an RFI from an electrical contractor regarding problems with an electrical panel. They are having problems terminating the feeder cables for a panel (120/208v,3phase,4wire, with a 225 Main Circuit Breaker). The cables are too large and the panel or the main circuit breaker cannot be modified to accomodate them. The panel is being fed through a 112.5kva transformer from another panel. The feeder is 4-600kcmil AWG and 1-#4/0 AWG Gnd. in 3.5" EMT conduit. I believe the sizing is correct.
I was told by a senior electrical engineer that he has never heard of any such problems like this during construction. Any advice/ideas as to why the feeder will not fit into the main breaker would be helpful.Is it simply that the panel that is being used is not capable of such a large feeder size? Thank you!
I was told by a senior electrical engineer that he has never heard of any such problems like this during construction. Any advice/ideas as to why the feeder will not fit into the main breaker would be helpful.Is it simply that the panel that is being used is not capable of such a large feeder size? Thank you!