Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

electrical power during grid connection

Status
Not open for further replies.

usman74

Electrical
Dec 7, 2014
14
i'm looking to find an answer about grid connection of nuclear power plant.
in over plant, there is limit for thermal power 45 MW (16 MWe) whenever generator connected to grid. why we need that minimum power???
is this due to reverse power????
 
Replies continue below

Recommended for you

I am not a Nuclear Power Station expert and not a thermal engineer.
Since this is not an electric issue but a thermo-nuclear problem actually, I think it is not the scope of this forum.
However, Fossil Power Station Boiler could not operate below 15% [as far as I know].So, I think, the boiler limits minimum power.
In the following article- for instance-for a nuclear unit of 900 MW the minimum 5% it would be required [45 MW].
 