Reesh14
Electrical
- Aug 3, 2005
- 38
I am working on an electrical service upgrade at an administration building. The power utility company is scheduled to provide 800A, 120/208V, 3phase service. An 800A MDP is being installed and will feed the other panels in the building. After design development, a server room was added and it increased the load approx. 250A. A 400A panel w/ shunt trip main breaker will be installed in the server room and serve all the IT equipment and HVAC equipment. The MDP does not have anymore breaker space nor can fit a 400A breaker. The plan is to provide a 400A enclosed breaker and tap into the main lug of the MDP or into the incoming service. I am assuming for now that the increase in load for the server room does not require us to increase the incoming service. The contractor suggested to tap the feed ahead of the main. Right now the plan is to use 2 parallel 500 sized wires from the utility transformer and into the MDP. I am not sure of how this should be tapped. If the server room panel should tap into the main lug of the MDP or at the incoming service (ahead of the main), will the 500's be enough to handle this or should they be increased to parallel 750's? I am not familiar with how feeds can be tapped and at what point this should be done. Any help would be much appreciated, thanks!