thinker
Electrical
- Aug 2, 2001
- 247
Please help to resolve a critical situation.We supplied to
the customer Variable Speed Drive system. The input main
circuit breaker is equipped with the standard shunt trip
device (120VAC) which opens circuit breaker when its coil
is energized. The customer does not accept this device
stating that the usage of shunt trip is a violation of NEC,
NFPA since this is not a fail safe solution. The customer
suggests that only de-energizing should be used (probably,
using undervoltage trip device).Please advise whether the
customer is right. Otherwise, why standard shunt trips exist? Our understanding was that shunt trip should be powered by independent reliable feeder, but this still does
not seem to be a fail safe system (in terms of broken wire
situation). I would appreciate if anyone with a proper
knowledge of electrical standards brings clarity in this issue.
the customer Variable Speed Drive system. The input main
circuit breaker is equipped with the standard shunt trip
device (120VAC) which opens circuit breaker when its coil
is energized. The customer does not accept this device
stating that the usage of shunt trip is a violation of NEC,
NFPA since this is not a fail safe solution. The customer
suggests that only de-energizing should be used (probably,
using undervoltage trip device).Please advise whether the
customer is right. Otherwise, why standard shunt trips exist? Our understanding was that shunt trip should be powered by independent reliable feeder, but this still does
not seem to be a fail safe system (in terms of broken wire
situation). I would appreciate if anyone with a proper
knowledge of electrical standards brings clarity in this issue.